HomeMatic CCU Heating Thermostat and Switch-actuator

Verfasst: 14.12.2022, 17:45
von clabbe2000
Hi, a question? When I put my thermostat in the off position I don't want the heat to come on, but it does now and starts the heating even in this off position.
What shall i do? Blocked the switch actuator in the off position on the thermostat?
Best Regards Claes L

Re: HomeMatic CCU Heating Thermostat and Switch-actuator

Verfasst: 14.12.2022, 18:03
von Baxxy
I think this is because the frost protection.
It's always active even if the thermostat is off.
You coult try to "lock" the actuator via WebUI-Program. In german the option is named "Sperrung aktiv".
This should prevent that the thermostat can switch the actor.

I have never testet ist, so try it out for yourself. :wink:

Re: HomeMatic CCU Heating Thermostat and Switch-actuator

Verfasst: 14.12.2022, 19:22
von clabbe2000
Ok thank you!
I will try this!
Best Regards
//Claes 😃

Re: HomeMatic CCU Heating Thermostat and Switch-actuator

Verfasst: 19.12.2022, 01:04
von elijen
Do you have the heating unit connected to Homematic (e.g. via Multi IO box)? If not the heater doesn't know whether there is demand for heat or not.

Re: HomeMatic CCU Heating Thermostat and Switch-actuator

Verfasst: 20.12.2022, 16:03
von clabbe2000
Hello
The thermostat is connected to a switch actuator
if you looked at my picture!(no multi io box).
Regards from
Claes