Direct Device Connection 105155 & 132030 using CCU2

Beitrag von sjo » 31.12.2014, 18:35

Hi,

I am struggling to configure my Homematic system as most of the documentation is in German. I hope that somebody on this forum will be able to help me. If more convenient please answer is German I will be able to translate.

My problem is the following:

I have got a big room in which two radiators are distant of 10 meters. Both radiators are equiped with 105155 thermostatic valves. One of the radiator is in a hole in the ground. The temperture sensor is of course incorrect.
In order to prevent this issue I have bought a wall thermostat 132030.

The idea was to ask the radiators to heat until the thermostat that is in the center of the room reachs a given temperture. I try to use the "Direct Device Connection" of my CCU2 to achieve that but without success. The 3 devices are still independent.
What I would like to achieve is that the wall thermostat controls the thermostatic valves. i.e. when I set the temperture on the wall thermostat to 21° the radiators heat until 21° is reached at the place of the wall thermostat.

Do I need to create a program to acheive that behaviour? What is the easiest way?

Any help would be welcome.

Thnak you in advance.

Homematicbeginner
Beiträge: 374
Registriert: 13.07.2013, 10:46
Wohnort: Rheinhessen
Hat sich bedankt: 3 Mal
Danksagung erhalten: 5 Mal

Re: Direct Device Connection 105155 & 132030 using CCU2

Beitrag von Homematicbeginner » 31.12.2014, 19:07

Hi,
in the actual CCU Software you should find the new Function "Group". Add. all 3 Devices into one Group and the System will create automatically all connections.
Important: If you use an additionall Software, change the settings allways in the group. Edit your Temperture Profile only in the group and not in the valve.
Homematicbeginner

sjo
Beiträge: 2
Registriert: 31.12.2014, 18:19

Re: Direct Device Connection 105155 & 132030 using CCU2

Beitrag von sjo » 01.01.2015, 12:48

Hi,

Thank you so much. it seems to work with your solution!

Happy New Year !

Homematicbeginner
Beiträge: 374
Registriert: 13.07.2013, 10:46
Wohnort: Rheinhessen
Hat sich bedankt: 3 Mal
Danksagung erhalten: 5 Mal

Re: Direct Device Connection 105155 & 132030 using CCU2

Beitrag von Homematicbeginner » 01.01.2015, 14:12

No Problem, Happy New Year.
Homematicbeginner

HenrikDK
Beiträge: 3
Registriert: 30.11.2017, 10:46

Re: Direct Device Connection 105155 & 132030 using CCU2

Beitrag von HenrikDK » 30.11.2017, 14:44

Found this 'old' answer ......... as i understand, when i have a room with 3 thermostats (105155), 2 windows contacts (131775) and 1 wall-termostat (132030), and these 6 devices are put into the same group, the system automatically know, that the wall-thermostat controle the 3 radiator thermostats, and that the 2 window contacts have to communicate with the wall-thermostat?????
Sounds almost to good to be true .... :D :-)

Best regards
Henrik - Denmark