Hi,
I am struggling to configure my Homematic system as most of the documentation is in German. I hope that somebody on this forum will be able to help me. If more convenient please answer is German I will be able to translate.
My problem is the following:
I have got a big room in which two radiators are distant of 10 meters. Both radiators are equiped with 105155 thermostatic valves. One of the radiator is in a hole in the ground. The temperture sensor is of course incorrect.
In order to prevent this issue I have bought a wall thermostat 132030.
The idea was to ask the radiators to heat until the thermostat that is in the center of the room reachs a given temperture. I try to use the "Direct Device Connection" of my CCU2 to achieve that but without success. The 3 devices are still independent.
What I would like to achieve is that the wall thermostat controls the thermostatic valves. i.e. when I set the temperture on the wall thermostat to 21° the radiators heat until 21° is reached at the place of the wall thermostat.
Do I need to create a program to acheive that behaviour? What is the easiest way?
Any help would be welcome.
Thnak you in advance.
Direct Device Connection 105155 & 132030 using CCU2
Moderator: Co-Administratoren
-
- Beiträge: 374
- Registriert: 13.07.2013, 10:46
- Wohnort: Rheinhessen
- Hat sich bedankt: 3 Mal
- Danksagung erhalten: 5 Mal
Re: Direct Device Connection 105155 & 132030 using CCU2
Hi,
in the actual CCU Software you should find the new Function "Group". Add. all 3 Devices into one Group and the System will create automatically all connections.
Important: If you use an additionall Software, change the settings allways in the group. Edit your Temperture Profile only in the group and not in the valve.
in the actual CCU Software you should find the new Function "Group". Add. all 3 Devices into one Group and the System will create automatically all connections.
Important: If you use an additionall Software, change the settings allways in the group. Edit your Temperture Profile only in the group and not in the valve.
Homematicbeginner
Re: Direct Device Connection 105155 & 132030 using CCU2
Hi,
Thank you so much. it seems to work with your solution!
Happy New Year !
Thank you so much. it seems to work with your solution!
Happy New Year !
-
- Beiträge: 374
- Registriert: 13.07.2013, 10:46
- Wohnort: Rheinhessen
- Hat sich bedankt: 3 Mal
- Danksagung erhalten: 5 Mal
Re: Direct Device Connection 105155 & 132030 using CCU2
No Problem, Happy New Year.
Homematicbeginner
Re: Direct Device Connection 105155 & 132030 using CCU2
Found this 'old' answer ......... as i understand, when i have a room with 3 thermostats (105155), 2 windows contacts (131775) and 1 wall-termostat (132030), and these 6 devices are put into the same group, the system automatically know, that the wall-thermostat controle the 3 radiator thermostats, and that the 2 window contacts have to communicate with the wall-thermostat?????
Sounds almost to good to be true ....
Best regards
Henrik - Denmark
Sounds almost to good to be true ....
Best regards
Henrik - Denmark