Hello,
I am planning to install a Homematic IP system with radiator thermostats in a three-storey house with thick tuff stone walls.
My intention is to use one HmIP-HAP as the main Access Point and, if necessary, add up to two additional HAP units to improve wireless coverage on the other floors.
I would prefer to use dedicated Access Points as signal extenders rather than plug-in devices such as the HmIP-PS or HmIP-PSM, because the electrical installation is divided into separate circuits for each floor, making the use of smart plugs as repeaters inconvenient.
I have a few questions:
1. Is it possible to use one HmIP-HAP as the main Access Point and add up to two additional HAP units to extend coverage?
2. What is the maximum number of additional HAPs officially supported when using the standard Homematic IP Access Point and app, without a CCU3?
3. Do the additional HAPs need to be connected to the main unit via Ethernet, or can they communicate wirelessly?
4. Can the radiator thermostats on each floor communicate with the nearest HAP, with the system automatically routing commands through the appropriate Access Point?
5. Are there any differences in these limitations between the HmIP-HAP and the newer HmIP-HAP2?
Has anyone implemented a similar setup in a multi-storey house with thick stone walls?
Thank you for your help.
Homematic IP – Using up to two additional HAPs to extend wireless coverage across three floor
Moderator: Co-Administratoren
-
Gerti
- Beiträge: 3643
- Registriert: 28.01.2016, 18:06
- System: CCU
- Wohnort: Hürth
- Hat sich bedankt: 23 Mal
- Danksagung erhalten: 380 Mal
Re: Homematic IP – Using up to two additional HAPs to extend wireless coverage across three floor
Hi!
1. Yes
2. 3
3. Ethernet, Same Network
4. It uses the Routing HAP, If communication to the Main HAP is unstable.
5. No
Gerti
1. Yes
2. 3
3. Ethernet, Same Network
4. It uses the Routing HAP, If communication to the Main HAP is unstable.
5. No
Gerti
Re: Homematic IP – Using up to two additional HAPs to extend wireless coverage across three floor
Thanks a lot, Gerti!
Just to be sure about point 2: does “3” mean three additional HAPs (four in total), or three HAPs in total including the main one?
And regarding point 4: is the switch to the routing HAP automatic and per device? For example, would the thermostats on the top floor consistently use the HAP on their floor if the link to the main HAP is weak?
I'd love if you could spend two words on my other question on this forum
Just to be sure about point 2: does “3” mean three additional HAPs (four in total), or three HAPs in total including the main one?
And regarding point 4: is the switch to the routing HAP automatic and per device? For example, would the thermostats on the top floor consistently use the HAP on their floor if the link to the main HAP is weak?
I'd love if you could spend two words on my other question on this forum