Hello
I have the CCU2 witch mostley control my radiators at the moment. I have both classic Homematic HM-CC-RT-DN and H-IP HMIP-eTRV thermostats.
My problem is that I can't get the right value for valve condition for my new Homematic IP thermostats. It shows 4% all the time in the diagrams, for my old classic thermostats I have no problem getting the the right value for valve condition.
Anyone else that has this problem, and maybe have a solution for it? It would really help me adjust the radiators.
My firmware is 2.25.15
Best regards
Joel
Valve condition CCU2/Homematic IP 4%
Moderator: Co-Administratoren
-
- Beiträge: 12434
- Registriert: 19.03.2014, 00:37
- System: in Planung
- Hat sich bedankt: 105 Mal
- Danksagung erhalten: 380 Mal
Re: Valve condition CCU2/Homematic IP 4%
Hi Joel,
Valve_State -> translated as "Ventilposition"
Level -> translated as "Ventil-Öffnungsgrad" (Value: 0 to 1.05)
For your diagram you have to use "Ventil-Öffnungsgrad"
Greetings
Bruno
Download "HmIP_Device_Documentation", there are two different parameters 2.3.2.1Joelbit hat geschrieben:... a solution ...
Valve_State -> translated as "Ventilposition"
Level -> translated as "Ventil-Öffnungsgrad" (Value: 0 to 1.05)
For your diagram you have to use "Ventil-Öffnungsgrad"
Greetings
Bruno