Re: Switch boiler HomematicIP
Verfasst: 28.02.2018, 13:52
Issue is solved!
I placed a wall thermostat to make sure all radiator thermostats have the same IST temperature
This results in comparable opening of the valves
I now used the 'and' function for turning off the boiler, and the 'or' function for turning on the boiler. Now the boiler switches on when at least one of the valves has an opening of more then 0.03 (3%) en switches off when all valves are opening equal or less then 0.03 (3%) Already with 3% opening the water starts flowing in my system.
Thanks for the help!
I placed a wall thermostat to make sure all radiator thermostats have the same IST temperature
This results in comparable opening of the valves
I now used the 'and' function for turning off the boiler, and the 'or' function for turning on the boiler. Now the boiler switches on when at least one of the valves has an opening of more then 0.03 (3%) en switches off when all valves are opening equal or less then 0.03 (3%) Already with 3% opening the water starts flowing in my system.