Verfasst: 04.04.2023, 11:13
Good morning,
I'm trying to finish my homematic underfloor heating installation, but so far only partial sucess unfortunately.
My setup is next, I have one FALMOT-C12 with 6 heads / valves connected via Access Point (and of course each room has own HmIP-STHD sensor). Also, I have connected WHS2 to Siemens RVP200 to control pump via external switch connection. That setup should work like that :
Default state of OUT2 on WHS2 is NC, i.e. it's closed and Siemens RVP200 works on "normal" mode (because it's closed), i.e. it runs a pump, mix hot water from central pipe, etc - i.e. normal behavior
Once rooms are heated enough WHS2 should open circuit and that should move RVP200 into standby mode.
HmIP-STHD works fine with combination with FALMOT-C12, I can see that valves are open and closed (partially) when it's required, issue is WHS2. I have tested and find out that WHS2 needs difference of 0.5 grad Celsius in order to change OUT state, i.e. I need to have 21.5 grad (21 is requested for example) in order for WHS2 to open circuit.
Did somebody faced same issue? Any solution for that with AccessPoint based installation or CCU3 will be a solution only?
P.S. Did you guys ever tried to contact Homematic Support? I had 2 technical (one is about this issue) cases and all I got is "Planning and setup must be carried out by a qualified person, as local conditions, manufacturer specifications and standards as well as the infrastructure used must be taken into account.". I have selected this product based on some criteria's and availability of support was one of that. Is it like that always with them?
Thank you
I'm trying to finish my homematic underfloor heating installation, but so far only partial sucess unfortunately.
My setup is next, I have one FALMOT-C12 with 6 heads / valves connected via Access Point (and of course each room has own HmIP-STHD sensor). Also, I have connected WHS2 to Siemens RVP200 to control pump via external switch connection. That setup should work like that :
Default state of OUT2 on WHS2 is NC, i.e. it's closed and Siemens RVP200 works on "normal" mode (because it's closed), i.e. it runs a pump, mix hot water from central pipe, etc - i.e. normal behavior
Once rooms are heated enough WHS2 should open circuit and that should move RVP200 into standby mode.
HmIP-STHD works fine with combination with FALMOT-C12, I can see that valves are open and closed (partially) when it's required, issue is WHS2. I have tested and find out that WHS2 needs difference of 0.5 grad Celsius in order to change OUT state, i.e. I need to have 21.5 grad (21 is requested for example) in order for WHS2 to open circuit.
Did somebody faced same issue? Any solution for that with AccessPoint based installation or CCU3 will be a solution only?
P.S. Did you guys ever tried to contact Homematic Support? I had 2 technical (one is about this issue) cases and all I got is "Planning and setup must be carried out by a qualified person, as local conditions, manufacturer specifications and standards as well as the infrastructure used must be taken into account.". I have selected this product based on some criteria's and availability of support was one of that. Is it like that always with them?
Thank you